Gentlemen,
Would it be possible (in accordance to the NEC) to size a MCC bus below the value obtained by : 125% of largest motor FLA + all others FLA if I have the right OCPD ? Let's say :
I have a MCC that feeds : 15x 50hp + 1x 100hp = 15x65A + 1,25x124A = 1099A. However, I choose a 800A bus with a Main Fuse Disconnect Switch of 800A to protect that bus. Of course, If I do that it's because I know all the motors won't be full load at the same time. Am I violating the NEC ?
Thanks guys