I have recently been given a new annual PM to clean and to retourqe the bussing on our mcc's at our three locations. One has a GE 8000 Line 480 V, another has an older Westinghouse 120/208V (Not sure of the model), the third had an older Westinghouse G O BHI 21500 IT 1 with a Cutler Hammer Freedom 2100 add-on all 120/208V. This is a new area for me. I have just gone over to the maintenance side from 8 years of construction, industrial and heavy commercial. And there is really no-one here at my location that has any formal electrical training, other than myself. Is this something that is normally done in-house or is it something that is typically contracted out? If done in house how detailed do you get in cleaning the bussing and how do you access it? Any help would be greatly appreciated. :?:blink::?
Ok, firstly I do have some experience on this but it may not be specifically how you all are gearing up to do this.
1) You would need to coordinate with the local POCO to have the power turned off for the specific time that it would take to perform the PM. There is not valid reason to attempt this while the systems are energized. If someone tells you thats not true...have them do it !
2) Typically you would simply set your torque device to the verified settings of the equipment and if none are present then view NEC Annex I and/or UL 486A-B for guidance and reading prior to doing any PM on this equipment. be careful as re-torquing does not mean over-tightening terminations...the T device should click close to the existing settings if done correctly originally even if pre AA8000 AL is encountered.
3) If the process requires local inspection (if did in the jurisdiction I worked in) then you need to coordinate that with the inspection department as it will likely be an after hours inspection and will cost extra.
4) Most of the time we used a compressed air system to blow out dust and so on and just recheck terminals, existing insulation and bracing of conductors if present, look for overheated terminations, damaged insulation at termination and so on.
Again yours may be different...but thats all that took place for PM's when we inspected them. And we really did nothing more than look at it and ask "are you done" and when the company doing the PM said yes we issued a ticket to permit the power company to reconnect and wait for the next PM.
Of course that was the standard practice for Switchboards and so on on, if the MCC can be isolated with proper PPE and put in a safe condition with LO/TO then refer to NFPA 70E for more details on a good procedure.