Hello, My name is Kenneth Lovasz.
I am currently inspecting some equipment manufactured in China to see if it's suitable work use in the US. I have a particular question about this MCC house used on an oilfield drilling Land rig. My question pertains to NEC 1999 (I don't have 2005 yet) Article 110-26. Spaces About Electrical Equipment.
It states that:
Sufficient access and working space shall be provided and maintained about all electric equipment to permit ready and safe operation and maintenance of such equipment. Enclosures housing electrical apparatus that are controlled by lock and key shall be considered accessible to qualified persons.
(a) Working Space. Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the dimensions of (1), (2), and (3) or as required or permitted elsewhere in this Code.
Table 110-26(a). Working Spaces
Minimum Clear Distance (ft)
Nominal Voltage to Ground Condition 1 Condition 2 Condition 3
??0?150 3 3 3
151?600 3 31/2 4
Looking at table 110-26(a) it says that the distance should be 42 inches, but I don't know if it applies in this instance.
Less than half of this MCC is accross from a metal bulkhead that is 38.58" away.
This is actually a pretty good MCC and none of the components in the MCC can be accessed while energize without bypassing two interlocks. The connections of the MCC are accessible, however the only reason one would access this while the MCC is energized would be to take amp readings. There is also an Ammeter provided on the front of each MCC can, (Though it's not very accurate). Does an MCC fall under the category as "likely to require examination, adjustment, servicing, or maintenance while energized"? My concern is the 38.58 Inch measurement to the one part of the wall across from the MCC. Does this comply or not?
I have a drawing but do not know how to post it here.
Any help would be greatly appreciated.
[ November 26, 2005, 09:05 PM: Message edited by: ettek ]
I am currently inspecting some equipment manufactured in China to see if it's suitable work use in the US. I have a particular question about this MCC house used on an oilfield drilling Land rig. My question pertains to NEC 1999 (I don't have 2005 yet) Article 110-26. Spaces About Electrical Equipment.
It states that:
Sufficient access and working space shall be provided and maintained about all electric equipment to permit ready and safe operation and maintenance of such equipment. Enclosures housing electrical apparatus that are controlled by lock and key shall be considered accessible to qualified persons.
(a) Working Space. Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the dimensions of (1), (2), and (3) or as required or permitted elsewhere in this Code.
Table 110-26(a). Working Spaces
Minimum Clear Distance (ft)
Nominal Voltage to Ground Condition 1 Condition 2 Condition 3
??0?150 3 3 3
151?600 3 31/2 4
Looking at table 110-26(a) it says that the distance should be 42 inches, but I don't know if it applies in this instance.
Less than half of this MCC is accross from a metal bulkhead that is 38.58" away.
This is actually a pretty good MCC and none of the components in the MCC can be accessed while energize without bypassing two interlocks. The connections of the MCC are accessible, however the only reason one would access this while the MCC is energized would be to take amp readings. There is also an Ammeter provided on the front of each MCC can, (Though it's not very accurate). Does an MCC fall under the category as "likely to require examination, adjustment, servicing, or maintenance while energized"? My concern is the 38.58 Inch measurement to the one part of the wall across from the MCC. Does this comply or not?
I have a drawing but do not know how to post it here.
Any help would be greatly appreciated.