... There is an ongoing argument about the fault withstand requirement of a gear when it is assured that it will only be fed from multiple sources for a transitional time only. According to anecdotal information this is an accepted assumption in EU.
It isn't anecdotal in IEEE 666,
Design Guide for Electric Power Service Systems for Generating Stations. Section 4.6.1 specifically allows this arrangement and equpiment rating.
I don’t know how the battle currently rages but I was in the thick of it for four Code cycles (‘96-‘05). I gave up personally trying to do anything in 2002.(See Proposal below) I was a member of API’s NEC Task Force when they tried their final shot in 2005.
The issue arises from the literal text in the first sentence of Section 110.9. While none of the principal switching devices in a basic closed-transition scheme will actually be called on to interrupt “…the current that is available at the line terminals of the equipment,” the computed available current still includes the contribution of both sources.
In theory though, down steam overcurrent devices would potentially need to be capable of interrupting the full available fault current. However, when I said that the potential was “infinitesimal” in my Proposal substantiation, I meant it. Statistically, the generally accepted age of the earth is not long enough for the required fault event to have happened once – even with a 2-second closed-transition.
CMP 1 knows this; API submitted the calculations in the 99 Code cycle. The Panel didn’t dispute the calculations; they just said that 2-seconds was unsubstantiated.
I only knew two of the Panel members at the time. One of them actually agreed with us in ‘99; the other was somewhat ambivalent. With the recent addition of a few more “Users” to argue the case within the Panel, the tide may change - but I don’t see any feet in the door this time around.
For some reason, CMP 1 just wants to keep throwing the responsibility to the AHJ. (Maybe they were frightened by the IEEE Standard's number) The basic problem with leaving it to the AHJ’s plan checkers or inspectors is that most of them don’t understand the issue. When it is explained to them they instantly opt for the more conservative interpretation, since it is “safer.”
By intuition, it may be. However, while I am usually willing to draw a very clear line between “SAFE” and “UNSAFE” without considering the cost, “SAFER” should also be cost effective since Section 90.1 says the NEC is to be “practical.”