Hello all, got a troubleshooting issue I am trying to figure out.
I have a switchboard feeding 480V MCC sections with 800A main lugs via a parallel feed. This section includes 3 - 150HP pump motors, then a 40HP and some random 5HP buckets.
Essentially, we had A & C phase fusing blow on the feeders for this MCC section. Initially, the feeders (cable running from the switchboard to the MCC section, just for clarity) were megged bad with the first try, then good with the second. We brought in a seperate testing contractor to megger everything again and the cables passed, but were in the Mega-ohm range whereas most of our good rated cable touches tera-ohm. Megger tests were done with all three phases at once, then each phase individually, all test "satisfactory".
Replaced fusing, threw the switch and checked voltage/current at the 800A main lugs for the section. Voltage checked fine on all three phases. However, there is an amperage difference on both the A & C runs of cable.
IE, one of the parallel runs is roughly 50A higher on the A phase than the other. The same occurs on the C phase, but its closer to 30A. To make matters worse, both of the parallel runs are seperated by conduit and it seems one has an issue on A, and the OTHER has the issue on C.
So, "run 1" has A phase 50A higher than "run 2" and "run 2" has C phase 30A higher than "run 1".
I am having someone come in to do IR scans on the switch feeding the MCC section soon. Other than that, I admit I am somewhat at a loss.
I assume I have a hot spot or a breakdown in insulation on some pieces of cable, but the fact that there is no "commonality" has me wary. I hate the idea or ripping out and running new, to find the same issue.
There were no voltage issue, and I am going to try shutting off the buckets one by one, checking amperage on phases after each to see if I can find something downstream. I also think we should seperate the parallel feeds and re-megger each individual cable as well.
Fun fun. Any other ideas greatly appreciated... thanks
I have a switchboard feeding 480V MCC sections with 800A main lugs via a parallel feed. This section includes 3 - 150HP pump motors, then a 40HP and some random 5HP buckets.
Essentially, we had A & C phase fusing blow on the feeders for this MCC section. Initially, the feeders (cable running from the switchboard to the MCC section, just for clarity) were megged bad with the first try, then good with the second. We brought in a seperate testing contractor to megger everything again and the cables passed, but were in the Mega-ohm range whereas most of our good rated cable touches tera-ohm. Megger tests were done with all three phases at once, then each phase individually, all test "satisfactory".
Replaced fusing, threw the switch and checked voltage/current at the 800A main lugs for the section. Voltage checked fine on all three phases. However, there is an amperage difference on both the A & C runs of cable.
IE, one of the parallel runs is roughly 50A higher on the A phase than the other. The same occurs on the C phase, but its closer to 30A. To make matters worse, both of the parallel runs are seperated by conduit and it seems one has an issue on A, and the OTHER has the issue on C.
So, "run 1" has A phase 50A higher than "run 2" and "run 2" has C phase 30A higher than "run 1".
I am having someone come in to do IR scans on the switch feeding the MCC section soon. Other than that, I admit I am somewhat at a loss.
I assume I have a hot spot or a breakdown in insulation on some pieces of cable, but the fact that there is no "commonality" has me wary. I hate the idea or ripping out and running new, to find the same issue.
There were no voltage issue, and I am going to try shutting off the buckets one by one, checking amperage on phases after each to see if I can find something downstream. I also think we should seperate the parallel feeds and re-megger each individual cable as well.
Fun fun. Any other ideas greatly appreciated... thanks