Scafremon
New member
- Location
- Orange, CA, US
I have purchased a new MCC. Plans call for 480Y/277 3P4W MCC, which makes sense, as in addition to the many 3W loads, there are a few 4W loads throughout the lineup. It is being fed from a swbd with 4 wires. It is not service entrance.
The manufacturer has advised that they are only providing a neutral bus in the incoming section - not a full length neutral bus as I was expecting.
For the loads that have 4 wires, the mfg advises that the contractor can run his neutral wire through multiple vertical sections over to the incoming section where the neutral pad is located, and terminate his neutral there. This appears to comply with 430.97 (A), based on the exception, as long as the barrier requirement is met. But I am still concerned if there might be some other code violation.
Once concern is section labeling. I would think that any section that does not have a neutral bus located within it will have to be labeled as 3P3W. We will therefore have disconnects for 4 wire loads located in vertical structures labeled as 3P3W.
Do you see any code concerns?
The manufacturer has advised that they are only providing a neutral bus in the incoming section - not a full length neutral bus as I was expecting.
For the loads that have 4 wires, the mfg advises that the contractor can run his neutral wire through multiple vertical sections over to the incoming section where the neutral pad is located, and terminate his neutral there. This appears to comply with 430.97 (A), based on the exception, as long as the barrier requirement is met. But I am still concerned if there might be some other code violation.
Once concern is section labeling. I would think that any section that does not have a neutral bus located within it will have to be labeled as 3P3W. We will therefore have disconnects for 4 wire loads located in vertical structures labeled as 3P3W.
Do you see any code concerns?