All industrial facilities should have sufficient documentation and labeling to meet 225.32 Exception 1, so this is not a code issue, it is an operational issue that is up to the facility. Having a main breaker at the MCC may serve some useful operational purpose depending on the type of facility. In a continuous process plant we shut down MCCs every 5 years, so for us it is not worth the cost and the additional device to maintain, whether the MCC is 5 feet from the switchgear that feeds it or 800 feet away in another building.
From the client's perspective, main breakers cost money and serve no power system protection purpose*, so why would the client want to pay for one? Whatever protection is provided by the main can be provided instead by the upstream device, which can be 400 feet away in a different building.
I'm assuming from the OP that the "power distribution panel/Switchgear" that is feeding the MCC is the same voltage as the MCC and therefore will have a branch circuit device that can provide the equivalent protection that a main breaker in the MCC would provide. If you have your heart set on a local disconnect device you can use a metal enclosed switch, but that's just as pointless as a main breaker.
*A main breaker on the secondary side of a unit substation transformer with a 15 kV or 5 kV feed to a 480V step down transformer is an exception. Some facilities use MCCs coupled to transformers like this without switchgear/switchboards/panelboards in between, and in this case a main should definately be provided. A lower cost solution is a "virtual main" that uses CTs on the secondary side that feed a protective relay on the primary, but there are some downsides to this scheme:
- It will clear slower than a MCCB or ICCB on the secondary
- this involves additional transformer switching that will reduce the life of the transformer
- many facilities do not have the sophistication to understand and maintain this scheme - it is bringing elements of MV relaying down into the 480V world, which may not be acceptable at some locations