Looking for some guidance on an MCC sizing/capacity issue. Here is the situation:
There is an existing 600 amp MCC with several loads, all HVAC units, fans and pumps. The MCC itself is fed by a 600 A breaker and (2) #400 wires per phase.
The plan is to remove most of the equipment and replace it with 2 large package units. It appears that the panel was overloaded already, per the loads below:
Electrician is telling me that the max load we can put on the MCC is 80% or 480 amps. Is this correct?
I was hoping we can feed our new AC units out of the MCC and re-feed the smaller loads that need to remain from elsewhere. Any thoughts?
Thanks!
There is an existing 600 amp MCC with several loads, all HVAC units, fans and pumps. The MCC itself is fed by a 600 A breaker and (2) #400 wires per phase.
The plan is to remove most of the equipment and replace it with 2 large package units. It appears that the panel was overloaded already, per the loads below:
Existing Equipment | HP | MCA | Fuse size | Comments |
AH-1 | 40 | 80 | To be demo'd | |
AH-2 | 40 | 80 | To be demo'd | |
EF-1 | 10 | 30 | To be demo'd | |
EF-2 | 10 | 30 | To be demo'd | |
PD-1 | 3 | 8 | To remain | |
PD-2 | 3 | 8 | To remain | |
ACP-1 | 3 | 8 | Abandoned | |
CU-1 | 117 | 150 | To be demo'd | |
CU-2 | 117 | 150 | To be demo'd | |
CU-3 | 117 | 150 | To be demo'd | |
CU-4 | 117 | 150 | To be demo'd | |
AC-1 | 41 | 60 | To remain |
Electrician is telling me that the max load we can put on the MCC is 80% or 480 amps. Is this correct?
I was hoping we can feed our new AC units out of the MCC and re-feed the smaller loads that need to remain from elsewhere. Any thoughts?
Thanks!