Gentlemen,
MCC BUS
I am wondering if the way I think about how to size MCC, Cable et switchboard breaker is right. Lets say I have a 480V MCC with twelve 50hp motors and a 100hp motor. So, by the values in table 430.250 and by article 430.24 , the bus rating shall not be less than :12x65A + 1x124x1,25 = 935A . I consider that the bus is "the conductor that supply several motors..."
For the overcurrent protection device (based on 430.62) the main breaker of the MCC shall not be greater than the OCPD of the biggest motor + FLA of other motors. Let's assume that I've used fast acting fuses on the 100hp, 175% of 124A = 217A + all other FLA : 217A + 12x65A = 997A
So, I could chose a 1200A bus with main breaker of 1000A. Make sense ? What if I plan to add load in the future and go for a 1600A bus. I would not have the right to put a main breaker of 1600A (cause I know I will need it) even if every bucket in my MCC has its own OCPD... ?
Cable Size from switchboard to MCC
Could the ampacity of the cable that feeds the MB of the MCC be rated according to the connected load ? or HAS (make sense if I plan to add load) to be rated according to the bus size ? Let's say I go with 1200A, as I consider my facitlity as a Supervised Industrial Installation, 240.91 says that feeder cable shall be rated not less than 95% of the "load" so I could go with 3x3c500MCM for 1140A (which is exactly 95% of 1200)... Right ?
Any help will be really apprecitated,
Thanks guys
MCC BUS
I am wondering if the way I think about how to size MCC, Cable et switchboard breaker is right. Lets say I have a 480V MCC with twelve 50hp motors and a 100hp motor. So, by the values in table 430.250 and by article 430.24 , the bus rating shall not be less than :12x65A + 1x124x1,25 = 935A . I consider that the bus is "the conductor that supply several motors..."
For the overcurrent protection device (based on 430.62) the main breaker of the MCC shall not be greater than the OCPD of the biggest motor + FLA of other motors. Let's assume that I've used fast acting fuses on the 100hp, 175% of 124A = 217A + all other FLA : 217A + 12x65A = 997A
So, I could chose a 1200A bus with main breaker of 1000A. Make sense ? What if I plan to add load in the future and go for a 1600A bus. I would not have the right to put a main breaker of 1600A (cause I know I will need it) even if every bucket in my MCC has its own OCPD... ?
Cable Size from switchboard to MCC
Could the ampacity of the cable that feeds the MB of the MCC be rated according to the connected load ? or HAS (make sense if I plan to add load) to be rated according to the bus size ? Let's say I go with 1200A, as I consider my facitlity as a Supervised Industrial Installation, 240.91 says that feeder cable shall be rated not less than 95% of the "load" so I could go with 3x3c500MCM for 1140A (which is exactly 95% of 1200)... Right ?
Any help will be really apprecitated,
Thanks guys