Long time listener, First time caller.
I am working a job where we are replacing (2) 75Hp pumps with (2) 200HP Pumps on VFD drives. There is an existing Centerline 2100 480V 600A MCC that I was hoping to reuse, but everything I have researched points to this not being a possibility. While digging through this job I was wondering what allows a vertical bus of the MCC to be rated at 300A when protected by a 600A main on the horizontal bus? Is it 240.21(B)(1)? Just want to understand where this comes from in code. This 300A vertical bus should limit a motor that can be installed on it to 125HP as FLA=156A*175%(time delay NEC30.52) = 273A, even though the continuous load would be evaluated as 156A*125%= 195A.
Thanks!
I am working a job where we are replacing (2) 75Hp pumps with (2) 200HP Pumps on VFD drives. There is an existing Centerline 2100 480V 600A MCC that I was hoping to reuse, but everything I have researched points to this not being a possibility. While digging through this job I was wondering what allows a vertical bus of the MCC to be rated at 300A when protected by a 600A main on the horizontal bus? Is it 240.21(B)(1)? Just want to understand where this comes from in code. This 300A vertical bus should limit a motor that can be installed on it to 125HP as FLA=156A*175%(time delay NEC30.52) = 273A, even though the continuous load would be evaluated as 156A*125%= 195A.
Thanks!