I am looking at installing a new circuit in an existing MCC. The MCC has a horizontal buss rating of 600A and a vertical rating of 300A. I understand that the main breaker to the panel is sized to protect the horizontal buss and should be 600A. However, all I can come up with for protecting the vertical buss is common sense must be used. Is there anything written that shows good judgment in sizing the breakers installed off of the vertical buss?
Can you place a 300A breaker on the vertical 300A rated buss that already has 2 150A breakers installed? I can't find anything that says you can't. I am afraid to check the main breaker rating, because it is not tripping and I can't see us not being very close to 600A.
Any guidance?