Fly-Guy5
Member
- Location
- Saginaw County, MI
Hello,
I'm a 10 year aprentice electrician and Bicsi cabling dude.
My question relates to Grounding and bonding in a new MDF I am working on.
The building is a 911 call center and has a large radio tower.
The MDF has a raised floor, 2 cabinet network data racks, 1 open 2 post network rack cor the Motorola tower radio communucation equipment and a second enclosed rack for radio equipment.
I had the electrician bond the raised floor to the a TMGBB.
I installed cable tray along the wall and out onto the top of my network cabinets and the 2 post radio cabinet ( the smaller enclosed radio cabinet is not in place yet) and bonded the tray and cabinets to the TMGBB.
I bolted the tray directly to my network cabinets and to the 2 post radio cabinet.
All according to ANSI/J-STD-607, TIA-942 and IEEE Std. 1100-2005 and the panduit grounding and bonding training.
Now, The Motorola tech wants me to remove the tray from touching any of his equipment (6"away) and wants me to remove it from my racks (6") so no cable tray touches the racks according to his Motorola specs?
The tray is still bonded to the bus-bar.
The racks are all bonded to the Bus-bar.
His radio tower cables enter the room and then go to overcurrent protection modules and bond to a bus bar that has a #4 running accross the room to the TMGBB.
The racks and floor are all bonded to the bus-bar.
What is the reasoning and code that would have me unbond the tray from the racks???
I think he or Motorola is bonkers..
Thanks
I'm a 10 year aprentice electrician and Bicsi cabling dude.
My question relates to Grounding and bonding in a new MDF I am working on.
The building is a 911 call center and has a large radio tower.
The MDF has a raised floor, 2 cabinet network data racks, 1 open 2 post network rack cor the Motorola tower radio communucation equipment and a second enclosed rack for radio equipment.
I had the electrician bond the raised floor to the a TMGBB.
I installed cable tray along the wall and out onto the top of my network cabinets and the 2 post radio cabinet ( the smaller enclosed radio cabinet is not in place yet) and bonded the tray and cabinets to the TMGBB.
I bolted the tray directly to my network cabinets and to the 2 post radio cabinet.
All according to ANSI/J-STD-607, TIA-942 and IEEE Std. 1100-2005 and the panduit grounding and bonding training.
Now, The Motorola tech wants me to remove the tray from touching any of his equipment (6"away) and wants me to remove it from my racks (6") so no cable tray touches the racks according to his Motorola specs?
The tray is still bonded to the bus-bar.
The racks are all bonded to the Bus-bar.
His radio tower cables enter the room and then go to overcurrent protection modules and bond to a bus bar that has a #4 running accross the room to the TMGBB.
The racks and floor are all bonded to the bus-bar.
What is the reasoning and code that would have me unbond the tray from the racks???
I think he or Motorola is bonkers..
Thanks