ten 50 amp subpanels needed averaging 30-40 amp loads. How would the MDP load be caculated by the SDP circuit breakers, or the sum total amps or watts of sub panels.
Fifty 9K Air-conditioners will be installed at a large K-span building. THe 9K air-conditioner is rated at 6.9 amps 115V specified a 15A CB, 6.9 X 115 = 793.5 watts The largest load is heating a resistive load no 125% for largest motor caculated. So 793.5 X 50 = 39,677 watts divided by 360 for 3 phase load = 110.208 X 125% = 137.760.
A 150 AMP service is needed a 4C 1/0 with #6 ground is needed correct.
These units have been specified, and a dedicated SDP has been specified for air-conditioners
This is a additional SDP for a large building, it is only for air conditioners loads. I want to caculate the total air condition load, then service, then feeders for service.
Originally Posted by Dbronx
Fifty 9K Air-conditioners will be installed at a large K-span building. THe 9K air-conditioner is rated at 6.9 amps 115V specified a 15A CB, 6.9 X 115 = 793.5 watts The largest load is heating a resistive load no 125% for largest motor caculated. So 793.5 X 50 = 39,677 watts divided by 360 for 3 phase load = 110.208 X 125% = 137.760.
A 150 AMP service is needed a 4C 1/0 with #6 ground is needed correct.
This is a additional SDP for a large building, it is only for air conditioners loads. I want to caculate the service, then feeders .
For us to be able to chip-in, can you tabulate your loads per feeder. It would be a lot easier that way than wording it all out.:?:?