J jml123 New member Location Fredericksburg Jun 24, 2015 #1 What is the maximum height of a breaker when installed in a main distribution panel? We also request the code article in which this answer can be found.
What is the maximum height of a breaker when installed in a main distribution panel? We also request the code article in which this answer can be found.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jun 24, 2015 #2 Center of the operating handle must not exceed 6'7" above the floor or work platform. As always, there are exceptions NEC 404.8
Center of the operating handle must not exceed 6'7" above the floor or work platform. As always, there are exceptions NEC 404.8