Multi Unit Apt bldg has both 125a and 100a load centers. It is cheaper to purchase a 24cct 125a MB panel than a 24cct 100a, as well as simplifies the installation if all panels are the same. If I installed a 100a breaker at the corresponding meter stacks, which are in the electric closets on each floor, and fed the tenant load centers with 100amp wiring (#1 alum), is this compliant? I tend to think the 100amp breakers at the meter stacks are the OCP, and sized accordingly for the wiring.....and the 125a MB in the loadcenter would be considered a disconnecting means.
 
Multi Unit Apt bldg has both 125a and 100a load centers. It is cheaper to purchase a 24cct 125a MB panel than a 24cct 100a, as well as simplifies the installation if all panels are the same. If I installed a 100a breaker at the corresponding meter stacks, which are in the electric closets on each floor, and fed the tenant load centers with 100amp wiring (#1 alum), is this compliant? I tend to think the 100amp breakers at the meter stacks are the OCP, and sized accordingly for the wiring.....and the 125a MB in the loadcenter would be considered a disconnecting means.

I agree with Don's view, but I wonder why you are using MB load centers as opposed to MLO. Is this a local requirement to have a main breaker?
 
inspector is concerned that the 100amp breaker at the meter stack will trip in lieu of the 125amp main breaker at the load center should a fault occur.....and the meter stacks are located in locked electrical closets, which would require maintenance to be contacted to open the room. I can't find anything code related that would prohibit my proposed installation.
 
inspector is concerned that the 100amp breaker at the meter stack will trip in lieu of the 125amp main breaker at the load center should a fault occur.....and the meter stacks are located in locked electrical closets, which would require maintenance to be contacted to open the room. I can't find anything code related that would prohibit my proposed installation.
I forgot about that rule. The inspector may have valid point. Look at 240.24(B).
 
I forgot about that rule. The inspector may have valid point. Look at 240.24(B).

True, but since this is a multiple-occupancy building, wouldn't the exception in (2008 NEC) 240.24(B)(1)(1) take affect? I have done many apartment buildings and Condo's that have meter stacks in a centralized electrical room and have never had an inspector say anything about 24024(B).
 