Why does 250.50 say "structure served" and not "structure supplied" ? . Does served mean a service ? . Does 250.50 apply to a second building supplied by a feeder from a first building ? . Or does the electrode requirement for the second building only come from the wording found in 250.32 ? . The second building does not have to be considered to be a "structure served" in order for 250.32 to apply. . If 250.50 doesn't apply to the feeder supplied second building, 250.32 would still require an electrode.
This has direct implications for a pool subpanel pedestal [and other situations also]. . If the absence of a service at the pool pedestal means that it is not a "structure served", 250.50 doesn't apply. . 250.32 would also not apply which would mean an electrode is not required for any non service pedestal, light pole base, or whatever.
Is there any ROP, ROC wording that addresses "structure served" for a building that is supplied by a feeder or branch circuit(s) ?
This has direct implications for a pool subpanel pedestal [and other situations also]. . If the absence of a service at the pool pedestal means that it is not a "structure served", 250.50 doesn't apply. . 250.32 would also not apply which would mean an electrode is not required for any non service pedestal, light pole base, or whatever.
Is there any ROP, ROC wording that addresses "structure served" for a building that is supplied by a feeder or branch circuit(s) ?