1)Is a means of disconnect switch required to be installed within sight for a CAT scan machine? 517(a) says it shall be provided in the supply circuit. 517(B) says in needs to be readily accessible from the X-Ray control.
There is a note on the manufacture spec's that it is 'desired' to install one, if not then the pwr can shutoff from the mcb.
The mdp is approx. 100' away and not within sight.
2) I believe the CAT scan machine is defined as a Fixed X-Ray Equipment. Is this correct?
I sized the conductor ampacity and ocpd not less than the Momentary ratings of the machine. The momentary rating are <40KVA at 480V 3phase. I used a 50A cb with #8AWG.
please advise