Hi all,
This is from the 2014 NYC Building Code (which is the current building code for NYC):
"1006.2.1 Sensors and controls. Automatic, occupant sensor or photosensor lighting controls shall be permitted within means of egress, provided that the illumination level is not reduced to a level below the minimum requirements of Section 1006.2, and the switch controllers are equipped for fail-safe operation ensuring that if the sensor or control fails, the lighting levels will beat the levels required by Section 1006.2."
Here is the lighting levels required by 1006.2:
1006.2 Illumination level. The means of egress illumination level shall not be less than 1 foot-candle (11 lux) at the walking surface.
My question is:
Can i still have a light switch, in addition to the ceiling occupancy sensor, on the wall that shuts the lights COMPLETELY off? or does that violate 1006.2.1?
This is from the 2014 NYC Building Code (which is the current building code for NYC):
"1006.2.1 Sensors and controls. Automatic, occupant sensor or photosensor lighting controls shall be permitted within means of egress, provided that the illumination level is not reduced to a level below the minimum requirements of Section 1006.2, and the switch controllers are equipped for fail-safe operation ensuring that if the sensor or control fails, the lighting levels will beat the levels required by Section 1006.2."
Here is the lighting levels required by 1006.2:
1006.2 Illumination level. The means of egress illumination level shall not be less than 1 foot-candle (11 lux) at the walking surface.
My question is:
Can i still have a light switch, in addition to the ceiling occupancy sensor, on the wall that shuts the lights COMPLETELY off? or does that violate 1006.2.1?