Does anyone see anything wrong with our means of support
You need another one within 12 inches of the boxDoes anyone see anything wrong with our means of support?View attachment 16072View attachment 16073
Sent from my iPhone using Tapatalk
You need another one within 12 inches of the box![]()
Looks like there's already a couple staples there just waiting...You need another one within 12 inches of the box![]()
Within 12" is correct.I thought it was nine inches.......
334.30 Securing and Supporting. Nonmetallic-sheathed
cable shall be supported and secured by staples, cable ties,
straps, hangers, or similar fittings designed and installed so
as not to damage the cable, at intervals not exceeding 1.4 m
(41⁄2 ft) and within 300 mm (12 in.) of every outlet box,
junction box, cabinet, or fitting. Flat cables shall not be
stapled on edge.
...
What are you covering the walls with? That box looks like it's over an inch past the face of the 2x4.
8 inches applies to a one gang box with no clamp, all multi-gang or other type of boxes need a clamp.I thought it was nine inches.......
314.17(C) Exception8 inches applies to a one gang box with no clamp...
Does anyone see anything wrong with our means of support?View attachment 16072View attachment 16073