Dispatched to a business this morning... found 6-11A at the incoming cable company service and going to the 12AWG ground which is clamped to the meter channel.
Service size 3P 120/208V 200A service in a body shop. Looking back I shoulda checked line to line voltage...
today's Line voltage read 130/113/120 to Ground - a little off but looking at the transformers on the pole I'm guessing that playing a part.
- Remove the ground from the meter channel = zero current measured.
- unplugged the energy from the modems, and the load side of the cable company connection no change in readings.
- tightened all panel connections.
- checked for grounding lock nut where service conductors enter the load center.
-turned off all the branch circuit breakers and current reading goes to zero.
-made sure had good ground to main water pipe. Metered 1.5-3A.
-Electric utility visited last week and taped up their connections.
-Cable utility had to replace their termination end because the insulation was melted.
-Tech who visited yesterday said got shock from cable termination. Nothing happened to me. and nothing measurable was present.
-load center desperately needs clean up and better yet replacement, as its filthy inside and 40 years old is my guess. Cloth covered SE conductors.
What are we missing?
Gotta be some wiring some where that needs repairs, a faulty piece of equipment, :blink:
Service size 3P 120/208V 200A service in a body shop. Looking back I shoulda checked line to line voltage...
today's Line voltage read 130/113/120 to Ground - a little off but looking at the transformers on the pole I'm guessing that playing a part.
- Remove the ground from the meter channel = zero current measured.
- unplugged the energy from the modems, and the load side of the cable company connection no change in readings.
- tightened all panel connections.
- checked for grounding lock nut where service conductors enter the load center.
-turned off all the branch circuit breakers and current reading goes to zero.
-made sure had good ground to main water pipe. Metered 1.5-3A.
-Electric utility visited last week and taped up their connections.
-Cable utility had to replace their termination end because the insulation was melted.
-Tech who visited yesterday said got shock from cable termination. Nothing happened to me. and nothing measurable was present.
-load center desperately needs clean up and better yet replacement, as its filthy inside and 40 years old is my guess. Cloth covered SE conductors.
What are we missing?
Gotta be some wiring some where that needs repairs, a faulty piece of equipment, :blink: