Hello and thanks, always, for your time.
A homeowner of a new-construction house (Florida) has been having her TV's power off intermittently, lights dim sometimes etc. So my first step is to see what branch-circuit drop is. At the outlets farthest from the panel I measure 123v@no load, 121v@minimal load, 114v@7A load and 101v@15A . The line is 15A OCPD so at 12A it would be dropping well over 10%.
I know the NEC recommends but does not mandate a 5% maximum drop, but Florida's building code (FBC Chapter 13) does mandate a 3% on branches (2%service drop/3%branch drop or reverse according to our local inspector).
I called the local inspector to ask if our location was subject to FBC chapter 13 and he said yes, absolutely. I then asked him how it should be measured (my guess would be 180VA/receptacle) and he told me that putting any load on the circuit in question is not how voltage drop is tested for that article. In his words: "Of course the voltage will drop if you're putting load on it, you need to measure the voltage drop across just the branch circuit wires, with no load connected. You want to measure the resistance of the branch circuit, not the load you attach to it".
I have been doing voltage drop calculations for many (too many) years and have never come across this method, and I'm a bit skeptical here. Also I believe that the language in FBC Chapter 13 states "design load".
So, question 1: Is this an accepted method of testing anywhere?
question 2: If the inspector is mistaken what is a recommended/professional way to proceed with the municipality in testing/enforcement?
thanks as always
A homeowner of a new-construction house (Florida) has been having her TV's power off intermittently, lights dim sometimes etc. So my first step is to see what branch-circuit drop is. At the outlets farthest from the panel I measure 123v@no load, 121v@minimal load, 114v@7A load and 101v@15A . The line is 15A OCPD so at 12A it would be dropping well over 10%.
I know the NEC recommends but does not mandate a 5% maximum drop, but Florida's building code (FBC Chapter 13) does mandate a 3% on branches (2%service drop/3%branch drop or reverse according to our local inspector).
I called the local inspector to ask if our location was subject to FBC chapter 13 and he said yes, absolutely. I then asked him how it should be measured (my guess would be 180VA/receptacle) and he told me that putting any load on the circuit in question is not how voltage drop is tested for that article. In his words: "Of course the voltage will drop if you're putting load on it, you need to measure the voltage drop across just the branch circuit wires, with no load connected. You want to measure the resistance of the branch circuit, not the load you attach to it".
I have been doing voltage drop calculations for many (too many) years and have never come across this method, and I'm a bit skeptical here. Also I believe that the language in FBC Chapter 13 states "design load".
So, question 1: Is this an accepted method of testing anywhere?
question 2: If the inspector is mistaken what is a recommended/professional way to proceed with the municipality in testing/enforcement?
thanks as always