Hi All,
First post. First of all, I want to thank you all for the knowledge I have gleaned from this forum. I've only been in the electrical field for a few years and MANY times I have come here to help beat the learning curve (which at times has been steep). So, thank you!
My question:
Does anyone have a formula or a trick of determining the circumference of a bundle of different diameter cables?
We are pulling in some medium voltage cable; two runs of (3) #750 AL & 1/0 CU ground and one run of (3) 4/0 AL & 1/0 CU ground. We need some new grips. Per Greenlee's Grip Selection Guide (Cooper's too), they say to "...bundle the cables together, measure the circumference and refer to chart..." That would work if we had the cable on hand. We won't get the cable until just before the pull but we were hoping to get the grips ahead of time. I could just get one grip for each cable but I'd rather bundle them up in one grip per pull.
Now, if all of the cables were the same diameter, Greenlee's selection chart works great (I can even do the math to figure that out). But the kicker comes in when adding the smaller diameter ground to the mix. By guesstimating, I could go too big or too small.
If anybody has a trick for calculating this, without cable in hand, I'd love to hear it. Sorry if I rambled or it the answer is so simple.
Thanks,
Tarjan
First post. First of all, I want to thank you all for the knowledge I have gleaned from this forum. I've only been in the electrical field for a few years and MANY times I have come here to help beat the learning curve (which at times has been steep). So, thank you!
My question:
Does anyone have a formula or a trick of determining the circumference of a bundle of different diameter cables?
We are pulling in some medium voltage cable; two runs of (3) #750 AL & 1/0 CU ground and one run of (3) 4/0 AL & 1/0 CU ground. We need some new grips. Per Greenlee's Grip Selection Guide (Cooper's too), they say to "...bundle the cables together, measure the circumference and refer to chart..." That would work if we had the cable on hand. We won't get the cable until just before the pull but we were hoping to get the grips ahead of time. I could just get one grip for each cable but I'd rather bundle them up in one grip per pull.
Now, if all of the cables were the same diameter, Greenlee's selection chart works great (I can even do the math to figure that out). But the kicker comes in when adding the smaller diameter ground to the mix. By guesstimating, I could go too big or too small.
If anybody has a trick for calculating this, without cable in hand, I'd love to hear it. Sorry if I rambled or it the answer is so simple.
Thanks,
Tarjan