- New Jersey
- Journeyman Electrician
Someone asked me this the other day and I would like some opinions regarding 210.52(C)(1)&(4). A 12" cabinet is placed with a 12" section of countertop to the side of a rangetop. The rangetop has a flange of about 5/8" leaving the counter space with a width of 11.375", is a receptacle required? So in other words does the width measurement begin at the hidden edge of the countertop or the edge of the rangetop?
210.52(C) Countertops. In kitchens, pantries, breakfast rooms,
dining rooms, and similar areas of dwelling units, receptacle outlets for countertop spaces shall be installed in accordance with 210.52(C)(1) through (C)(5).
(1) Wall Countertop Spaces. A receptacle outlet shall be installed at each wall countertop space that is 300 mm (12 in.)
or wider. Receptacle outlets shall be installed so that no point along the wall line is more than 600 mm (24 in.) measured
horizontally from a receptacle outlet in that space.
(4) Separate Spaces. Countertop spaces separated by
rangetops, refrigerators, or sinks shall be considered as
separate countertop spaces in applying the requirements of 210.52(C)(1). If a range, counter-mounted cooking unit, or sink is installed in an island or peninsular countertop and the depth of the countertop behind the range, counter mounted cooking unit, or sink is less than 300 mm (12 in.), the range, counter-mounted cooking unit, or sink shall be considered to divide the countertop space into two separate countertop spaces. Each separate countertop space shall
comply with the applicable requirements in 210.52(C).