It states in NEC Article 110.26(1) Depth of Working Space…is measured from the enclosure front. Now that couldlead you to believe they’re referring to the front enclosure cover. But thenyou see in Figure 110-20 illustrated in blue “Exposed Live Parts.” Table110.26(A)(1) Working Space list 3 Conditions all describing “Exposed LiveParts.” The Article goes on stating Rear and Sides…Work Space isn’t required.
After carefully examining allthese points it is now my interpretation that the statement “is measured fromthe enclosure front” does not indicate the front enclosure cover, butthe “Exposed Live Parts” located from the enclosure front. I think aclearer way of stating this would be…”is measured from the exposed live partsat the enclosure front.”
What is your interpretationplease?
After carefully examining allthese points it is now my interpretation that the statement “is measured fromthe enclosure front” does not indicate the front enclosure cover, butthe “Exposed Live Parts” located from the enclosure front. I think aclearer way of stating this would be…”is measured from the exposed live partsat the enclosure front.”