PhaseShift
I have been experiencing several problems lately with induced noise on low voltage DC systems. These problems have been occuring on 24V power systems and 4-20mA signal wires. Usually when these problems occur we just guess there is induced noise and end up having to change cable, move cable etc... I wanted to see if there was a way to acutally view the noise with an O-scope or something to see what was exactly causing problems.
If I were to hook an O-Scope up to these signals to look for this noise would I want to look at the voltage on these signals or the current or both?
For instance on case we have is were a 24V system is causing a false ground fault alarm on a processor when we know there is no ground fault present. We suspect noise. Would we want to look at this 24V voltage in this case to see if there was any evidence of noise and where it was coming from?
Another instance is where we have erratic readings on a 4-20mA signal If I wanted to look at this signal would I want to look at the voltage or the actual 4-20mA current signal on the cable with the scope? What would I want to look at to see what was causing the noise?