Measuring Power
Re: Measuring Power
If you are only using a clamp-on meter, you are only measuring amps. Depending on the type of clamp-on, it is either inclusive of harmonic content (true RMS type) or not (averaging type).
Re: Measuring Power
I agree with Ron. But to address your question, you are reading the amps associated with KVA, not just the amps associated with KW.
Re: Measuring Power
Ron
If the power factor is 1 then the amps x volts x 1.73 is the KVA which equals KW. If the PF is less than 1 then amps x volts x 1.73 = KVA and KVA x pf = KW.
[ April 27, 2005, 03:17 PM: Message edited by: bob ]
Re: Measuring Power
bob,
I appreciate the reply, although I sorta got that part straight in my head.
My point was that amps is amps whether your calculating kVA or kW. There is just the extra power factor term involved with kW as you properly pointed out.
Re: Measuring Power
Originally posted by ron: Charlie,
I'm confused. I would say it was amperage associated with both kVA and kW.
I won't say that your way of putting it is wrong, but I will say that it is redundant. The amps associated with KVA includes the amps associated with KW.
If you had a measured voltage value, you could take the measured current and calculate KVA. You could not also calculate KW without some additional information. That is why I said the amps were those associated with KVA, not with KW. Perhaps I should have said "not only with KW."