Rford1985
New User
- Location
- Indianapolis
- Occupation
- Journeyman Electrician / Service Tech / Estimator
My discussion/question is in regards to bonding mechanical equipment to the electrical service at a residential setting. Per Indiana Residential code, we are required to bond metallic gas lines and water lines. So typically, if I'm installing a 400amp service with (2) 200amp main breaker load centers, I would install a #4 grounding electrode conductor from each 200amp panel to grounding electrode(s) (groundrods). Then for gas/water lines, I would install a #4 from each panel to the gas line and a #4 from each panel to the water line. (so you end up with (2) #4's attached to the water line and (2) #4's at the gas line) My question is, is this actually necessary, or could I just run (1) #4 to gas and (1) #4 to water from one of the load centers, and then jump another set of #4's from 1st load center to the other? Hopefully my description/question isn't too confusing. Please let me know how you guys would typically do this...