ElectricJer
Member
- Location
- Sonoma County, CA
- Occupation
- Electrician
Has anyone seen multiple disconnects mechanically interlocked? I'd like to be able to disconnect and lock out multiple motors by throwing one lever. Thanks.
For that matter, you could use contactors to control any number of loads. The first thing that came to mind when I read the OP was a standard manual transfer switch.To wit; you can buy 6 pole disconnect switches, specifically for this purpose. Simultaneously disconnect 2 x 3phase motors, 3 x 240V single phase motors, or 6 x 120V single phase motors.
View attachment 2553136
Your instinct is correct, contactors are not allowable for LO/TO. You cannot padlock a contactor open. Shunt tripped breaker is fine, so long as the breaker is lockable.If I was calling this a "lock out" device.....I wouldn't be comfortable just interrupting control power to a bunch of motor starters. That would be cheap and easy to do. I'd be wanting what Jraef suggests and that wouldn't be cheap or easy to add after the fact. Not even sure I'd trust a shunt trip breaker feeding a MCC for "lockout" duty. But that comes closer IMHO.
Not a code guy so I can't say what is allowed.
I found those too, and they might be the best/safest option. The rub though, is that I need to disconnect 4, 3phase 480 motors, and I need it to be fairly quick and easy so that the line operator can lock it out, remedy the problem on the line, and then close the circuit back in. (I work for a saw mill) Using these 6 pole disconnects would me that I'll need two, which isn't terrible, but I like to think that there might be something better. Also the $5,745.00 ea. price tag is a bit outrageous.To wit; you can buy 6 pole disconnect switches, specifically for this purpose. Simultaneously disconnect 2 x 3phase motors, 3 x 240V single phase motors, or 6 x 120V single phase motors.
View attachment 2553136
Your instinct is correct, contactors are not allowable for LO/TO. You cannot padlock a contactor open. Shunt tripped breaker is fine, so long as the breaker is lockable.
I would say it is indirectly addressed by 430.109 in that a controller is not listed as an acceptable disconnect except as specified in (6).I vaguely remember seeing that contractors are not allowed as a means for disconnect, but I can't remember where I saw that. Do you know where that is in the code? (I scoured Article 430 NEC and couldn't find it. In fact, I was surprised by how vague that article was in describing means for disconnect)
I would say it is indirectly addressed by 430.109 in that a controller is not listed as an acceptable disconnect except as specified in (6).
Perhaps I'm thinking of LOTO requirements from another publication.
This happens often. Many people seem to believe that the LOTO procedures they follow are the only ones that exist.
I believe there are at least 3 different LOTO versions in OSHA publications, make sure you are following the one that pertains to your industry.
For example after opening and locking out a disconnect; to create an electrically safe work place, one needs to use a meter to verify the circuit is de-energized, however for a safe 'operator' action one may only need to verify the machine cannot restart.