hcubed
Member
- Location
- Boulder, CO
- Occupation
- PE
Hi Guys,
I'm working on an asphalt plant in Southern California. The contractor has run bare ACSR overhead for the plant 12.47kV distribution. The county plan checker is saying he can't allow it because the ACSR doesn't have a UL 1072 listing. He says the cable needs UL 1072 and an MV-90 or MV-105 rating. MV-90 and MV-105 are for insulated conductors only. We use that frequently for underground. Our overhead cable came from a reputable supplier and has the requisite ASTM listings for aluminium conductor.
This sort of bare overhead distribution is common for large industrial plants, and we've done it many times before. I can't find anything in the NEC that says overhead MV conductors must be insulated. I've studied section 310.60 thoroughly and can't find anything that indicates we're not to code. Any help with this pesky plan checker would be appreciated. Thanks.
I'm working on an asphalt plant in Southern California. The contractor has run bare ACSR overhead for the plant 12.47kV distribution. The county plan checker is saying he can't allow it because the ACSR doesn't have a UL 1072 listing. He says the cable needs UL 1072 and an MV-90 or MV-105 rating. MV-90 and MV-105 are for insulated conductors only. We use that frequently for underground. Our overhead cable came from a reputable supplier and has the requisite ASTM listings for aluminium conductor.
This sort of bare overhead distribution is common for large industrial plants, and we've done it many times before. I can't find anything in the NEC that says overhead MV conductors must be insulated. I've studied section 310.60 thoroughly and can't find anything that indicates we're not to code. Any help with this pesky plan checker would be appreciated. Thanks.