MANUEL MARTINEZ
Member
- Location
- mexico
I?m been asked to extend a 400 KCM, 23 KV, 100%BIL, EPR, line 450 meters with a 500 KCM, 23 KV, 133% BIL, EPR cable. I want to know if any restriction exist to join different insulation calbes Thanks
Short answer: If you have protection that will trip out any fault in less than 60 seconds then there is no concern.I?m been asked to extend a 400 KCM, 23 KV, 100%BIL, EPR, line 450 meters with a 500 KCM, 23 KV, 133% BIL, EPR cable. I want to know if any restriction exist to join different insulation calbes Thanks
Since there is only one current path, there is no reason that all parts be identical.Thanks for your answers, I wonder if parallels cables must have same insulation, a join of cables may have the same? I rather prefer to use the same cable it is already installed, any argument to convince my client.
You are right, big john, of course. See UL 1072 Table 13.1 or IEC 60502-2 4.1 Rated voltages. [Also EPRI EL-5036-V4 and ICEA S-68-516 and so on].
However the existing cable is 100% rated insulation and the
new extension is 133% that means ?better?. We don?t know if the supply voltage is 23 kV indeed. May be less?
In my opinion, the only problem is to find a suitable joint-including the splice.I think Raychem [TE now] could help to find one.![]()