I need information on how to terminate medium voltage cables (4160v) at the supply side and at the load side. Also what to use for equipment ground.
zog said:Call a certified MV cable installer. It isnt easy and doing it wrong can have very bad results.
alfonso1900 said:I need information on how to terminate medium voltage cables (4160v) at the supply side and at the load side. Also what to use for equipment ground.
The cable we are using is shielded and the thing i need to know is if i need to ground both ends or just the supply side. If so what do i do with the other end?. Where in the NEC do i get the size for the equipment ground?. is it just based on ampacity?.alfonso1900 said:I need information on how to terminate medium voltage cables (4160v) at the supply side and at the load side. Also what to use for equipment ground.
alfonso1900 said:The cable we are using is shielded and the thing i need to know is if i need to ground both ends or just the supply side. If so what do i do with the other end?. Where in the NEC do i get the size for the equipment ground?. is it just based on ampacity?.
what about shield currentes when both ends are grounded and the tempereture increase due to this currents?
Triplexed cables often contain EGC, otherwise size you EGC based on the main conductors ampacity.
weressl said:
- Shield is NOT to be used as EGC.
- Triplexed cables often contain EGC, otherwise size you EGC based on the main conductors ampacity.
weressl said:
- Both ends.
- Shield is NOT to be used as EGC.
- Triplexed cables often contain EGC, otherwise size you EGC based on the main conductors ampacity.
frenchelectrican said:EGC = Electrode Grounding Conductor.
AKA " earth " wire
Merci,Marc
weressl said:According to Raychem, with their kit even a caveman can do it......![]()
weressl said:
- Both ends.
- Shield is NOT to be used as EGC.
- Triplexed cables often contain EGC, otherwise size you EGC based on the main conductors ampacity.
steve66 said:If you terminate both ends of the sheild, exactly how do you not use it as an EGC?
Steve