I've read through the forums here on previous discussions of closed transition transfer schemes and necessary AIC and interrupting ratings.
There were a couple things that no one brought up, but I would still highly value opinions on for my application.
I'm not sure what voltage levels the previous thread was covering, but I'm dealing with a 4160V Main-Tie-Main scheme. Traditionally these use a barely open fast transition (3 cycle) "odd-man-out" scheme for manual transfer, and a voltage supervised open transition for automatic (utility line failure) transfer. This does not provide my client with adequate reliability, so we are looking into alternative transfer schemes.
For either closed transition or a permanent parallel, there is quite a bit of redesigning of the system required, and I've read the Buff Book thoroughly on the subject. However, the AIC and interrupting ratings are still causing me pause. Clearly 2xSC ratings would be required for a permanent parallel.
But for a very brief (a few cycles) closed transition, the previous discussion somewhat hinged on the statements
What no one brought up, as far as I could find, is what if we simply used the fault detection capabilities of a modern multifunction microprocessor relay to prevent closed (or any kind of) transfer if there was a fault inside the system? This is not difficult with today's relays. The system should never transfer for a downstream overcurrent event, and to do so would only compound the event. The system only needs to transfer for an upstream fault (often miles away on the utility grid), and should block any transfers on a downstream fault.
I understand utilities don't like you paralleling their feeds and backfeeding into a fault, but unless I am mistaken (the likelihood of which is why I'm posting here) fault current backfed to the grid will not approach the SC available inside the system. I base this belief on the assumption that impedances on the grid are much higher than inside the system, and that faults on the grid have to be detected by reverse current/power relays because the normal overcurrent relays (set lower than the available SC current) will not usually pickup for reverse current!
So... there's my thought process. I know there are other factors, but speaking only to the AIC and interrupting ratings, am I missing anything?
Thanks!
There were a couple things that no one brought up, but I would still highly value opinions on for my application.
I'm not sure what voltage levels the previous thread was covering, but I'm dealing with a 4160V Main-Tie-Main scheme. Traditionally these use a barely open fast transition (3 cycle) "odd-man-out" scheme for manual transfer, and a voltage supervised open transition for automatic (utility line failure) transfer. This does not provide my client with adequate reliability, so we are looking into alternative transfer schemes.
For either closed transition or a permanent parallel, there is quite a bit of redesigning of the system required, and I've read the Buff Book thoroughly on the subject. However, the AIC and interrupting ratings are still causing me pause. Clearly 2xSC ratings would be required for a permanent parallel.
But for a very brief (a few cycles) closed transition, the previous discussion somewhat hinged on the statements
andBut basically during that closed transition time your fault current may exceed the AIC ratings of your equipment. This is sometimes accepted as a "calculated risk".
If you are paralleling one live source with another live source, what are the odds of a bolted fault occurring during a 1-2sec transfer period?
What no one brought up, as far as I could find, is what if we simply used the fault detection capabilities of a modern multifunction microprocessor relay to prevent closed (or any kind of) transfer if there was a fault inside the system? This is not difficult with today's relays. The system should never transfer for a downstream overcurrent event, and to do so would only compound the event. The system only needs to transfer for an upstream fault (often miles away on the utility grid), and should block any transfers on a downstream fault.
I understand utilities don't like you paralleling their feeds and backfeeding into a fault, but unless I am mistaken (the likelihood of which is why I'm posting here) fault current backfed to the grid will not approach the SC available inside the system. I base this belief on the assumption that impedances on the grid are much higher than inside the system, and that faults on the grid have to be detected by reverse current/power relays because the normal overcurrent relays (set lower than the available SC current) will not usually pickup for reverse current!
So... there's my thought process. I know there are other factors, but speaking only to the AIC and interrupting ratings, am I missing anything?
Thanks!