Alangi1361
Member
- Location
- California
Alright, I am getting confused on NEC table 310.60(c) 79.
I have a MV switchgear with 4 feeders connected to it rated 600A.
We have the 4 conductors, 3 phase, + 2 additional in an underground duct bank.
Based on the NEC table mentioned above, if I want to have 6 conduits in underground bank( detail 3), and if I size conductors to be 750 (@4.16 KV, copper, type MV-105), the current ampacity will go down to 375A.
So, if with future expansion, I draw 450A from the conductor, I will have overcurrent situation. Now, if my CB is rated for 600 A, it will not detect the OC fault.
Would somebody help me with this dilemma?
Thanks.
I have a MV switchgear with 4 feeders connected to it rated 600A.
We have the 4 conductors, 3 phase, + 2 additional in an underground duct bank.
Based on the NEC table mentioned above, if I want to have 6 conduits in underground bank( detail 3), and if I size conductors to be 750 (@4.16 KV, copper, type MV-105), the current ampacity will go down to 375A.
So, if with future expansion, I draw 450A from the conductor, I will have overcurrent situation. Now, if my CB is rated for 600 A, it will not detect the OC fault.
Would somebody help me with this dilemma?
Thanks.