Is there an industry standard for the minimum depth and slope of medium voltage cable ductbanks? I am aware of the NEC article 310 requirements but wanted to see if there are other standards that I can reference.
Where the underground ducts run to manholes with sump pumps, I have seen specs that required 1/8" per foot of slope to the manholes so the water would drain to the manhole.