Hello-
Have not done much design work with 15KV equipment.
Voltage is 12470/7200V
Have a primary service coming from a vacuum circuit recloser (supplied by power company) to a metal enclosed switchgear with fused switches. Feeding a liquid filled 500KVA transformer with one of the switches. My question is regarding Neutral and ground. Do I need a neutral wire? Instinct tells me I only need (3) 15 KV MV-90 EPR cables. #2 is the minimum size cable at this voltage per table 300.106(A) which works because fuse size is only 50A, I use 200% for primary side protection, and according to 310.60(C)(77) #2 is good for 145A. I guess I do not understand the 7200V. Is that the line-to-line voltage, which does not make sense to me?
Finally, if no neutral is required (?) a ground certainly would be. How is the size of the ground determined? Circular mills of the #2 cable? Ampacity of the fuse? I would think circular mils of the cable otherwise the ground size would only be a #10 which does not seem correct to me at all.
Any articles I can read to help me understand are always appreciated.
Thanks for your reply
Have not done much design work with 15KV equipment.
Voltage is 12470/7200V
Have a primary service coming from a vacuum circuit recloser (supplied by power company) to a metal enclosed switchgear with fused switches. Feeding a liquid filled 500KVA transformer with one of the switches. My question is regarding Neutral and ground. Do I need a neutral wire? Instinct tells me I only need (3) 15 KV MV-90 EPR cables. #2 is the minimum size cable at this voltage per table 300.106(A) which works because fuse size is only 50A, I use 200% for primary side protection, and according to 310.60(C)(77) #2 is good for 145A. I guess I do not understand the 7200V. Is that the line-to-line voltage, which does not make sense to me?
Finally, if no neutral is required (?) a ground certainly would be. How is the size of the ground determined? Circular mills of the #2 cable? Ampacity of the fuse? I would think circular mils of the cable otherwise the ground size would only be a #10 which does not seem correct to me at all.
Any articles I can read to help me understand are always appreciated.
Thanks for your reply