Thought I read this in the NEC not long ago but can't find it now. Please point me to the article/section relating to installing or running medium voltage through buildings or structures. Thought I had read, "shall be in metallic/rigid conduit".
Thank you
Thanks for responding Bob.
Please allow me to expand. I have stumbled upon an indoor 15KV cable installation above the ceiling. This shielded cable is laying in a cable-tray and turning up and into a junction box where it is spliced. It is considered accessible. In fact, it can and has been walked on in several locations.
Your help has enabled me to find the area I was thinking would apply. Would like your opinion on using 110 Part III 110.31 (B)(1) as an argument, at least from a standpoint of safety.
Your thoughts?
(B) Indoor Installations.
(1) In Places Accessible to Unqualified Persons. Indoor electrical
installations that are accessible to unqualified persons
shall be made with metal-enclosed equipment.
Equipment. A general term, including fittings, devices, appliances,
luminaires, apparatus, machinery, and the like used as a
part of, or in connection with, an electrical installation.
NEMA VE 2-2013
1.2 GENERAL
WARNING!—Do not use a cable tray as a walkway, ladder, or support for people; cable tray is a mechanical support system for cables and raceways. Using cable trays as walkways can cause personal injury and can damage cable tray and installed cables.