medium voltage insulation

Status
Not open for further replies.

jcb730

Member
I am getting conflicting reports about 133% insulation level of medium voltage cable. Some people are stating that it only increases the fault current time from 1 minute (100%) to 1 hour (133%). Others are saying that it also increases the rated circuit voltage (5kv at 100% and up to 8Kv at 133%). If the second is true, does the labeling on the cable reflect the true voltage rating or not. I was referred to table 4-1 to ICEA. Any supporting information would be greatly appriciated. Thanks.
 
Some useful information:

Insulation level applies to what?s referred to as shielded cables or cables with an insulation shield. Generally cables rated at 5 kV and higher are shielded but some at 5 kV, depending on their construction, may be unshielded.

When choosing a cable?s voltage class it?s based on the phase to phase voltage of the system on which the cable is to be used. Cable voltage classes are standardized in North America and it?s standard practice to use the next higher cable class for a certain system voltage class. For example a 13.8 kV system uses a 15 kV rated cable and a 27.6 kV system uses a 28 kV rated cable and so on.

The insulation thickness and minimum conductor size for each voltage class is designed to limit the maximum voltage stress at the conductor shield surface and the average stress in the insulation wall. These stresses are calculated based on insulation thickness and on the phase to ground voltage that the insulation is subjected to. The voltage the insulation is subjected to during normal operation is the phase to phase voltage divided by sqrt 3 (1.73). This is the voltage across the insulation wall during normal operation all day long every day and this is the same for both wye and delta three phase systems.

If there is a fault somewhere on a three phase system the voltage in the system is disturbed because voltage on the faulted phase may go to zero or close to it and voltage on the other two phases rises. Theoretically this voltage rise can take the phase to ground voltage on the unfaulted phases up to the phase to phase voltage. This situation can persist until the fault is cleared or the system is de-energized. Therefore, choose a cable?s insulation level based on the fault clearing time of the system in which it?s used.

If fault is cleared one minute or less you can use 100% insulation level cable.

If fault clearing time is from one minute to one hour you should use 133% insulation level cable.

There is also a 173% insulation level but this is very uncommon. 173 % is used on systems where the fault clearing time is indefinite.

As the insulation level increases so does the insulation thickness for a given voltage class. For example, a 15kV 100%, XLPE insulated cable would have an insulation thickness of 0.175" ( 4.44 mm ). The same cable with 133% insulation level would have an insulation that?s 0.220" ( 5.59 mm ) thick. The 173% insulation level thickness is not specified by any recognized standard so we generally use the thickness for the 100% level for the next higher standard voltage class of cable. In this example we would go to 25 kV, 100% or a cable with 0.260" ( 6.60 mm ) of insulation.

The only exception to 100% vs 133% is the 5 kV cable class. In this case most North American standards specify 0.090" ( 2.29 mm ) for both insulation levels.

As you can see a higher insulation level cable generally has a thicker insulation. Insulation thickness for these levels is not a direct ratio of 100% to 133% but is related to limiting the electrical stress that the insulation sees before a fault is cleared. Controlling this stress will help prevent cables on the unfaulted phases from failing due to overvoltage while a fault may be present. If fault clearing time is longer, a chance of cable failure is increased so a higher insulation level is required.

Since 133% insulation level cables have an increased insulation thickness, they can be used in place of 100%, but the reverse is not true. Also electrical stress during fault and normal operating conditions is less in 133% insulated cable, therefore expected cable life will be increased. Because of this some users, especially utilities, specify 133% cable even though fault clearing time would allow 100%.

Generally 100% insulation level cable is used on grounded wye or star systems and 133% is used on delta systems. This is because generally a fault is cleared very quickly on a wye ( ie: within a few cycles) but could persist for longer periods on a delta system.

The real governing factor is fault clearing time. Up to one minute use 100%! Up to one hour use 133%

I beleive the standard which discusses the voltage rating is AEIC CS8.
 
Well stated kingpb, just to clarify it is the ground fault clearing time that needs to be considered. You did state that but it may not be clear to everyone so I wanted to point that out.
 
Well stated kingpb, just to clarify it is the ground fault clearing time that needs to be considered. You did state that but it may not be clear to everyone so I wanted to point that out.

I agree. Nicely stated.

Other than overvoltage, what other electrical stresses occur during L-G faults? How serious are magnetic forces on the L-G faulted cable?
 
Some useful information:

Insulation level applies to what?s referred to ------
QUOTE]

Very interesting explaination

See the below topic too

100 Percent Level,

Cables in this category may be applied where the system is provided with relay protection such that ground faults will be cleared as rapidly as possible, but any case within one minute. While these cables are applicable to the great majority of cable installations that are ground ed systems, they may be used also on other system for which the application of cables is acceptable provided the above clearing requirement are met in completely de-energizing the faulted section.

133 Percent Level,

This insulation level corresponds to that formerly designated for "ungrounded" systems. Cable in this category may be applied in those situations where the clearing time requirement of the 100 percent category can not be met, and yet there is adequate assurance that the faulted section will be de-energized in a time not exceeding one hour. Also, they may be used when additional insulation strength over the 100 percent level category is desirable

173 Percent Level,

Cables in this category should be applied on systems where the time required to de-energize a section is indefinite. Their use is recommended also for resonant grounded systems. Consult the cable manufacturer for insulation thickness.
 
Thanks for the info. So I make sure I get this right, a 25kv cable rated at 133 percent cannot be used on a 26.4kv system. A Kerite representive stated that as per table 4-1 with ICEA they would argue the point and win that with the 133% insulation that it would be acceptable. Thanks in advance.
 
medium voltage

medium voltage

Can a 25kv cable rated at 133% insulation level be used on a 26.4kv system. A Kerite representive stated that a per table 4-1 with ICEA they woul argue the point and win the it would be acceptable. It is my belief that the increased insulation level is to increase the fault current time. Thanks.
 
Thanks for the info. So I make sure I get this right, a 25kv cable rated at 133 percent cannot be used on a 26.4kv system. A Kerite representive stated that as per table 4-1 with ICEA they would argue the point and win that with the 133% insulation that it would be acceptable. Thanks in advance.


I haven't seen anyone agree or disagree. I'm not sure that is correct, but I don't know. If you only need a 100% insulation level, this might be OK. Seems like your cable rep would know what is acceptable.
 
Thanks for the info. So I make sure I get this right, a 25kv cable rated at 133 percent cannot be used on a 26.4kv system. A Kerite representive stated that as per table 4-1 with ICEA they would argue the point and win that with the 133% insulation that it would be acceptable. Thanks in advance.

Southwire also makes a cable that is listed for 25kV 133%, or 35kV 100% (grounded), but they also make a 28kV 100% rated.

Take a look at the Kerite data sheets, and verify what you are being told. You might also want to check pricing. It could be that a 28kV 100% is less than a 25kV 133% (35kV 100%). Also, installation could be a factor, make sure you look at O.D. and fill requirements. This could effect conduit sizing. Total installed cost could sway you one way or the other.
 