A customer has requested that we provide a meter for metering a 13.2kV switch. I have everything figured out with the exception of the primary connection of the PTs to the MV bus.
I have selected the PTs to use, but I was curious as the proper way to terminate the conductors on the primary side of the transformer. I've seen many 12.47kV (7.2kV L-G) meter installations that use a single unshielded conductor. I'm not sure this is right based on the 310.10(E) requirement for shielded conductors. With 13.2kV being 7.6kV to ground, I believe my only option is to use a shielded cable. Do I need stress cones? Any help is appreciated. Thanks.
I have selected the PTs to use, but I was curious as the proper way to terminate the conductors on the primary side of the transformer. I've seen many 12.47kV (7.2kV L-G) meter installations that use a single unshielded conductor. I'm not sure this is right based on the 310.10(E) requirement for shielded conductors. With 13.2kV being 7.6kV to ground, I believe my only option is to use a shielded cable. Do I need stress cones? Any help is appreciated. Thanks.