I need some help with NEC requirements for medium voltage (12.47kV) installations.
Situation: Existing building is getting an addition which requires additional capacity. The utility pole has a utility disconnect switch. There's an overhead service to a customer owned pole with a disconnect on top. The service goes down the pole in rigid conduit and underground to an existing vault. There is an existing, antiquated knife blade disconnect located in the vault on the primary side. Further down the wall is some fusing next to each transformer. The existing customer owned transformers are located in this transformer vault. (3 can type transformers) These are getting removed and a new pad mounted transformer is being located next to the vault.
The inspector is requiring a new disconnect, with adjacent OCP, on the primary side of the transformer that is "Listed as a Service Disconnecting Means compliant with NEC 230.205." and that "the Utility Service Point and customer owned Service Conductors could require the Primary Service Disconnect to be located at the Utility Pole or Property line."
I was planning on saving the customer some money and since there's a lot of extra space now in the tranformer vault I was going to install a non-enclosed, wall mounted, knife blade switch with all three ungrounded legs opening at the same time. The inspector told me they will not accept any type of switch located in the transformer vault. The vault is about 12'W x 18'L x 8'H.
1) If I'm replacing the transformer why do I need to upgrade the service disconnect? Isn't existing equipment grandfathered in?
2) Does UL even list medium voltage switches? Does NEC require this switch to be listed if nothing exists? I cannot find any information on the UL website about this type of equipment and none of the manufacturers I know about state that their equipment is UL listed. No one asked for evidence that the tranformer was UL listed during plan review. Why is the switch special.
3) I understand that a service entering a building needs a service disconnect at the point it enters, but I don't see anything about needing a disconnect at the property line when there's a customer owned transformer. Is this right?
Situation: Existing building is getting an addition which requires additional capacity. The utility pole has a utility disconnect switch. There's an overhead service to a customer owned pole with a disconnect on top. The service goes down the pole in rigid conduit and underground to an existing vault. There is an existing, antiquated knife blade disconnect located in the vault on the primary side. Further down the wall is some fusing next to each transformer. The existing customer owned transformers are located in this transformer vault. (3 can type transformers) These are getting removed and a new pad mounted transformer is being located next to the vault.
The inspector is requiring a new disconnect, with adjacent OCP, on the primary side of the transformer that is "Listed as a Service Disconnecting Means compliant with NEC 230.205." and that "the Utility Service Point and customer owned Service Conductors could require the Primary Service Disconnect to be located at the Utility Pole or Property line."
I was planning on saving the customer some money and since there's a lot of extra space now in the tranformer vault I was going to install a non-enclosed, wall mounted, knife blade switch with all three ungrounded legs opening at the same time. The inspector told me they will not accept any type of switch located in the transformer vault. The vault is about 12'W x 18'L x 8'H.
1) If I'm replacing the transformer why do I need to upgrade the service disconnect? Isn't existing equipment grandfathered in?
2) Does UL even list medium voltage switches? Does NEC require this switch to be listed if nothing exists? I cannot find any information on the UL website about this type of equipment and none of the manufacturers I know about state that their equipment is UL listed. No one asked for evidence that the tranformer was UL listed during plan review. Why is the switch special.
3) I understand that a service entering a building needs a service disconnect at the point it enters, but I don't see anything about needing a disconnect at the property line when there's a customer owned transformer. Is this right?