I need to test this. Does anyone know how to test? Can I use a 1000v megger if so does anyone have an idea of what the readings should look like. The manufacturer tech was no help. Thanks!
ANSI/NETA MTS-2011 has a procedure in Section 7.19.2 - Surge Arresters, Medium- and High-Voltage Surge Protection Devices There are later versions, but here is a copy of the 2011 http://www.iemworldwide.com/pdf/ansi-neta-mts-2011.pdf
That is exactly what I was looking for. I figured balanced resistance values was a pretty safe bet, but I wanted to verify as I have not done much with transient voltage suppression systems. Thank you!