Medium voltage tray cables and EGC
Dsg319
West Virginia
Wv Master “lectrician”
I know next to nothing with MV equipment and requirements.
But on a job where we pulled 6 parallel 3c750kcmil tray cables with and 1/0 ground in the cable.
This is 4160v and coming off of from what I can tell is a 3000amp breaker.
How do they get away with not having a 400kcmil EGC ?.
Even with utilizing cable tray as an EGC at the expansion joints it as 4/0 jumpers for continuity.
I know there has to be more to this than what I know.
Just looking to get educated.
I too believe it needs to be a 400 kCMIL conductor for the EGC, in accordance with Table 250.122.
250.122(A) - Last sentence
"Equipment grounding conductors shall be permitted to be sectioned within a multiconductor cable, provided the combined circular mil area complies with Table 250.122."
4160V conductor can have a concentric or shielding which acts like a fault current path back to the source where it is bonded at both ends. (250.190(C)(2)). The asterisk being that it is not a solidly grounded system and the shield is capable of clearing the fault before being damaged.
250.122(A) allows you to take the concentric + wire type egc as the size since it is all within the same cable.
Thank you!