I know next to nothing with MV equipment and requirements.
But on a job where we pulled 6 parallel 3c750kcmil tray cables with and 1/0 ground in the cable.
This is 4160v and coming off of from what I can tell is a 3000amp breaker.
How do they get away with not having a 400kcmil EGC ?.
Even with utilizing cable tray as an EGC at the expansion joints it as 4/0 jumpers for continuity.
I know there has to be more to this than what I know.
Just looking to get educated.