Installation of a 1000kw 13470V / 4160/2300 transformer. Do we bond the xo terminal even those it feeding a 700HP motor starter?
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
Installation of a 1000kw 13470V / 4160/2300 transformer. Do we bond the xo terminal even those it feeding a 700HP motor starter?
Installation of a 1000kw 13470V / 4160/2300 transformer. Do we bond the xo terminal even those it feeding a 700HP motor starter?
Being that you have a WYE secondary I would assume you want it grounded. Either at the transformer or the gear/disco
 