L LK61 Member Location KCMO Occupation Electrician Jul 14, 2023 #1 Installation of a 1000kw 13470V / 4160/2300 transformer. Do we bond the xo terminal even those it feeding a 700HP motor starter?
Installation of a 1000kw 13470V / 4160/2300 transformer. Do we bond the xo terminal even those it feeding a 700HP motor starter?
Dsg319 Senior Member Location West Virginia Occupation Wv Master “lectrician” Jul 14, 2023 #2 LK61 said: Installation of a 1000kw 13470V / 4160/2300 transformer. Do we bond the xo terminal even those it feeding a 700HP motor starter? Click to expand... LK61 said: Installation of a 1000kw 13470V / 4160/2300 transformer. Do we bond the xo terminal even those it feeding a 700HP motor starter? Click to expand... Being that you have a WYE secondary I would assume you want it grounded. Either at the transformer or the gear/disco
LK61 said: Installation of a 1000kw 13470V / 4160/2300 transformer. Do we bond the xo terminal even those it feeding a 700HP motor starter? Click to expand... LK61 said: Installation of a 1000kw 13470V / 4160/2300 transformer. Do we bond the xo terminal even those it feeding a 700HP motor starter? Click to expand... Being that you have a WYE secondary I would assume you want it grounded. Either at the transformer or the gear/disco
L LK61 Member Location KCMO Occupation Electrician Jul 16, 2023 #3 That’s what I was thinking but it’s nice having some feedback. Thanks