zemingduan
Senior Member
- Location
- Philadelphia,PA
- Occupation
- Electrical Designer
We have a job that has 13.2KV campus distribution system. Between buildings' pad mount transformers and the site MV switch gear, we need to run (4) 5"C conduit with concrete encased duct bank for the MV feeder.
1) What is the spacing requirements between the 5" MV conduits in the duct bank? Does it fall under NEC and should follow figure 310.60 (C) (3)? Or does it fall under NESC with other requirements?
2) What are the MV duct bank burial depth requirements? The NEC figure 310.60(C) (3) has the note in below screen shot. It says minimum burial depth per 300.50 and maximum 30" burial depth to the top of the duct banks. But I see many engineer electrical drawings specify Min. 36" burial depth to top of the MV electrical duct bank. Is it allowed and Why? If you MV duct bank burial Min. 36" , should NEC 310.60(B)(2) (b) derating factor apply?
Thanks!
1) What is the spacing requirements between the 5" MV conduits in the duct bank? Does it fall under NEC and should follow figure 310.60 (C) (3)? Or does it fall under NESC with other requirements?
2) What are the MV duct bank burial depth requirements? The NEC figure 310.60(C) (3) has the note in below screen shot. It says minimum burial depth per 300.50 and maximum 30" burial depth to the top of the duct banks. But I see many engineer electrical drawings specify Min. 36" burial depth to top of the MV electrical duct bank. Is it allowed and Why? If you MV duct bank burial Min. 36" , should NEC 310.60(B)(2) (b) derating factor apply?
Thanks!