I was looking at a datasheet for a 4.16kV Siemens VFD and I noticed that the VFD listed a Short Circuit Current Rating of 50kA for "100mSec maximum time release".
To me this looks like the VFD has a short circuit withstand rating of 50kA for approximately (6) cycles or 100mSec. Is this correct? I haven't seen many of these drives in application so I'm not sure if this is a somewhat typical value.
Does a MV VFD not have a "Momentary" rating similar to other MV devices which have both a withstand (or Interrupting) and a momentary or Close & Latch rating?
To me this looks like the VFD has a short circuit withstand rating of 50kA for approximately (6) cycles or 100mSec. Is this correct? I haven't seen many of these drives in application so I'm not sure if this is a somewhat typical value.
Does a MV VFD not have a "Momentary" rating similar to other MV devices which have both a withstand (or Interrupting) and a momentary or Close & Latch rating?