can someone direct me to any place that says
in WORDS, that you can put this voltage(15KV) in pvc conduit surface mounted(boiler room)THANKS GEO
 

charlie

Senior Member
Location
Indianapolis
Re: medium voltage

300.37 Aboveground Wiring Methods. Aboveground conductors shall be installed in rigid metal conduit, in intermediate metal conduit, in electrical metallic tubing, in rigid nonmetallic conduit, in cable trays, as busways, as cablebus, in other identified raceways, or as open runs of metal-clad cable suitable for the use and purpose. In locations accessible to qualified persons only, open runs of Type MV cables, bare conductors, and bare busbars shall also be permitted. Busbars shall be permitted to be either copper or aluminum.
 

friebel

Senior Member
Location
Pennsville, N.J.
Re: medium voltage

To: vanwalker, I know that you asked about putting your service in PVC conduit, of which you got an affirmative answer.
I would also like to suggest cable tray if that would fit your needs. Just a thought. I would always try to use cable tray wherever I could.
 

vanwalker

Senior Member
Location
lancaster
Re: medium voltage

THANKS GUYS! I could not get a definite YES from carlon? this question was ask of me.

[ December 11, 2003, 08:34 AM: Message edited by: vanwalker ]
 