Designing a new police station. There is a room we are labeling "training room" or "classroom". Its intended use is for staff education, both in the traditional classroom sense and also for light physical training (think hand-to-hand control scenarios). The building contains many conference rooms and a muster room, where presumably all the more conferency-type activities would be held.
Does the NEC require floor boxes here? Looking at 210.71 information note #1...
* designed or intended for gathering of seated occupants - so far yes, except for the times when the occupants are not seated
* for such purposes as conferences - no?
* deliberations - no?
* or similar purposes - maybe?
* where portable electronic equipment such as computers, projectors or similar equipment will likely be used - there will be a FIXED projector, and it easy to imagine a scenario where a few people have laptops.
Then information note #2 says examples of rooms that are NOT considered meeting rooms include auditoriums, school rooms, and coffee shops. This is obviously not an auditorium or coffee shop, and though is a classroom is not technically a schoolroom since it is not in a school.
/start of rant. Guys, I hate this code. Hate it. This instance is kind of pushing me over the top. At a recent new installation (different client) a staff member tripped over a "flush" floor box cover and went to the emergency room. I'm not looking forward to an officer getting hurt in a training exercise because they tripped or landed on one of these. My hatred of this part of the code has nothing to do with money and everything to do with unnecessarily overcomplicating what used to be a simple design decision. This code doesn't make anything safer - the floor boxes are more of a safety hazard than temporary extension cords IMO. We have floor boxes in some of our conference rooms and one in our training center - all installed by design, prior to the code requiring - and in four years not one of them has been used once. I'm fine with that being a design decision, but not fine with it being a code mandate. /end rant
I will request an interpretation from the local inspector, but am not optimistic. They follow code and although this may be a gray area it doesn't really allow an exception. Before I contact him I would appreciate hearing the wisdom of the crowd as to what "meeting room" discussions you have had with AHJs. Thank you in advance!
Does the NEC require floor boxes here? Looking at 210.71 information note #1...
* designed or intended for gathering of seated occupants - so far yes, except for the times when the occupants are not seated
* for such purposes as conferences - no?
* deliberations - no?
* or similar purposes - maybe?
* where portable electronic equipment such as computers, projectors or similar equipment will likely be used - there will be a FIXED projector, and it easy to imagine a scenario where a few people have laptops.
Then information note #2 says examples of rooms that are NOT considered meeting rooms include auditoriums, school rooms, and coffee shops. This is obviously not an auditorium or coffee shop, and though is a classroom is not technically a schoolroom since it is not in a school.
/start of rant. Guys, I hate this code. Hate it. This instance is kind of pushing me over the top. At a recent new installation (different client) a staff member tripped over a "flush" floor box cover and went to the emergency room. I'm not looking forward to an officer getting hurt in a training exercise because they tripped or landed on one of these. My hatred of this part of the code has nothing to do with money and everything to do with unnecessarily overcomplicating what used to be a simple design decision. This code doesn't make anything safer - the floor boxes are more of a safety hazard than temporary extension cords IMO. We have floor boxes in some of our conference rooms and one in our training center - all installed by design, prior to the code requiring - and in four years not one of them has been used once. I'm fine with that being a design decision, but not fine with it being a code mandate. /end rant
I will request an interpretation from the local inspector, but am not optimistic. They follow code and although this may be a gray area it doesn't really allow an exception. Before I contact him I would appreciate hearing the wisdom of the crowd as to what "meeting room" discussions you have had with AHJs. Thank you in advance!