A meeting room 1001 SF does not have any requirements for receptacle placement?
Am I reading correctly?
What was the thinking there?
That receptacle placement in commercial facilities is completely left up to the desires and needs of the tenant. Or probably more specifically, the receptacle placement in residential should be dictates to prevent unscrupulous contractors from cutting corners and to prevent extension cords run willy nilly in a residence.
210.71
"meeting room of not more than 1000SF"
The code requires the receptacle outlets in the small meeting rooms because the occupants will likely need power for their electronic devices.I think the idea was that having a lot of outlets in a meeting space increases the likelihood that people will either be distracted by plugged in devices, or leave something plugged in that causes a problem. So in a small room <1000 sq ft, they can decide to not allow it. But larger than that a custodian would not be able to safely use an extension cord for vacuums, floor machines etc., so they will need an outlet in the room.
Under the new section you are correct. However, remember that new rule is a method to determine the "amount" of receptacles and not the actual placement of those receptacles, except in meeting room that is at least 3.7 m (12 ft) wide and that has a floor area of at least 20 m2 (215 ft2) shall have at least one receptacle outlet located in the floor at a distance not less than 1.8 m (6 ft) from any fxed wall for each 20 m2 (215 ft2) or major portion of foor space.A meeting room 1001 SF does not have any requirements for receptacle placement?
Am I reading correctly?
What was the thinking there?
Under the new section you are correct. However, remember that new rule is a method to determine the "amount" of receptacles and not the actual placement of those receptacles, except in meeting room that is at least 3.7 m (12 ft) wide and that has a floor area of at least 20 m2 (215 ft2) shall have at least one receptacle outlet located in the floor at a distance not less than 1.8 m (6 ft) from any fxed wall for each 20 m2 (215 ft2) or major portion of foor space.
Otherwise, the placements of such receptacles are at the will of the designers or building owners.
Partially indicated here: even though larger rooms don’t need floor boxes...they must now have recepts at 12 ft intervals around then perimeter.
Prove It.....not how 210.71 is written in 2017 NEC.
It was clarified by CMP 2 that the intent of the reference to 210.52(A)(1) -(A)(4) is simply the means to determine the total number as defines in 210.71 (B). No intent was to imply a spacing requirement which is why the charging statement says they can be where ever the designer or owner chooses.
How / where can this be seen ? Open for all to read or only NFPA members ?
I have been laying out plugs like it was a residence also.
Here's an interesting article that might clear it up for you
https://iaeimagazine.org/magazine/2017/11/21/receptacle-outlet-requirements-for-meeting-rooms/
How / where can this be seen ? Open for all to read or only NFPA members ?
I have been laying out plugs like it was a residence also.
are you actually in a location that is using the 2017 NEC? I JUST started worrying about the costly requirements of the 2014.