The 2017 nec may have gone overboard on the rule requiring the number of receptacles in a meeting hall. Apparently, this is a proactive rule to avoid possible injuries.
A nice Mike Holt graphic
210.71 Meeting Rooms.
(A) General. Each meeting room of not more than 93 m2
(1000 ft2) in other than dwelling units shall have outlets for
nonlocking-type, 125-volt, 15- or 20-ampere receptacles. The
outlets shall be installed in accordance with 210.71(B). Where
a room or space is provided with movable partition(s), each
room size shall be determined with the partition in the position
that results in the smallest size meeting room.
Informational Note No. 1: For the purposes of this section,
meeting rooms are typically designed or intended for the gathering
of seated occupants for such purposes as conferences,
deliberations, or similar purposes, where portable electronic
equipment such as computers, projectors, or similar equipment
is likely to be used.
Informational Note No. 2: Examples of rooms that are not meeting
rooms include auditoriums, schoolrooms, and coffee shops
A nice Mike Holt graphic