Meg ohms to feet
Wyoming
Does anyone know of a calculation that would find the approximate length of wire for damaged underground? An example is if I were to meg a bad underground conductor, could I convert the reading to a footage, even if the wire is not completely broken? I greatly appreciate any help
Sent from my SM-A037U using Tapatalk
No, you can't. To many variables. Get a Fault Finder and you will never look back
Now you have my full attention. I've been looking into it but am still struggling to see how I could get a general footage or area to find a fault from a given point.
What is the total distance of the conductor run?
Is the earth the same type of soil the entire distance? Any sidewalks?
Are there any metallic piping systems in the area? Utility poles with ground rods? Has the neighbor run the sprinklers today? Etc.
A TDR might work in the right hands, but not straight out of the box with no experience. The fault finder will. Read the fine manual first.
As a theoretical matter, if you have a wire with a high resistance fault to ground:
you would measure the resistance to ground from either end.
This resistance is the sum of the wire resistance, the soil resistance, and the fault resistance.
If you assume that the soil resistance and the fault resistance are constant, then the difference between these two measurements is the wire resistance to the fault from either end.
You know the resistance per foot of wire, so you calculate distance from the wire resistance.
As a practical matter the above theory is pure bovine excrement. The soil resistance values are not constant. The fault resistance is probably not constant. And the wire resistance is so much smaller than the other two values, so the noise on your megohm measurement will swamp the milliohm wire resistance values.
If you have a solid wire to wire bolted fault then you can plausibly locate it with milliohm measurements.
There are better tools for the job.
One approach pulses high voltage into the wire, then you walk along the ground with a probe that detects the leakage.
Another approach uses the fact that signals travel in wire at a known speed, and is essentially radar but in the wire.
See the 'Fault Finder' mentioned by @ptonsparky or 'Time Domain Reflectrometry'
Jon
I remember seeing a Bell Labs prototype cable fault finder in the 1970s.
It was nearly the size of a steamer trunk and took two people to move.
I have no idea what it cost, but I'm quite sure it was a trifle more than $1555.
I used some kind if thing like that back in the 80's. There was some kind of battery powered device that sent out a pulse and a wand that looked like a metal detector. It kind of worked, but it wasn't the greatest. It was better than nothing though. I think it was also supposed to locate pipes
When in tech school, we had to learn Kirchhoffs law, the teacher said you could find the location of the fault. Never used it since.