Is it safe/ok to check a pool pump motor with a megohmeter?
If so what readings would be in the "pass" zone?
Had a customer call and ask me to check to see why his breaker is tripping for his pool pump. He said sometimes it will run for hours then trip and now he says it's gotten more frequent. Even to the point of only running a few minutes. He took it upon himself to put in a new GFCI breaker. He said that didn't help any.
I plan to check the current draw to see if I can catch it tripping to see if it's overloaded or not.
I thought if I couldn't catch it with my meter I would try a regular breaker to see if the tripping is on overload or ground fault. Of course this would be just to test and no one will be in or near the pool. If it still trips on the regular breaker I thought I could megger it but wasn't sure if it's ok to do that on a pool pump motor.
Now this pump is most likely a dual voltage motor. Meaning it can run off of 115V or 230V. It's been a while since I was there to remember for sure, but most if not all, the pool pump motors are dual voltage.
I'm assuming I would check:
hot to neutral
hot to frame of motor
neutral to frame
Any other ideas/suggestions?
If so what readings would be in the "pass" zone?
Had a customer call and ask me to check to see why his breaker is tripping for his pool pump. He said sometimes it will run for hours then trip and now he says it's gotten more frequent. Even to the point of only running a few minutes. He took it upon himself to put in a new GFCI breaker. He said that didn't help any.
I plan to check the current draw to see if I can catch it tripping to see if it's overloaded or not.
I thought if I couldn't catch it with my meter I would try a regular breaker to see if the tripping is on overload or ground fault. Of course this would be just to test and no one will be in or near the pool. If it still trips on the regular breaker I thought I could megger it but wasn't sure if it's ok to do that on a pool pump motor.
Now this pump is most likely a dual voltage motor. Meaning it can run off of 115V or 230V. It's been a while since I was there to remember for sure, but most if not all, the pool pump motors are dual voltage.
I'm assuming I would check:
hot to neutral
hot to frame of motor
neutral to frame
Any other ideas/suggestions?